7/11/2015 11:06 AM | |
Joined: 5/12/2006 Last visit: 5/14/2024 Posts: 22251 Rating: (2985)
|
Hello,
the SIMOTION C FW can be downloaded here: https://support.industry.siemens.com/cs/ww/en/view/31263919 Normaly the FW is stored on the card if you order it, you can check this if you open the Card in Windows explorer and check that the files are on the card. Download the FW an extract it in the root of the MMC then the C240 boot up correctly. Or it is a systemerror. Is there a project stored on the card? Regards Christoph |
Last edited by: ChristophD at: 7/11/2015 11:08:58 AMLast edited by: ChristophD at: 7/11/2015 11:16:23 AM |
|
7/11/2015 11:43 AM | |
Posts: 205 Rating: (11) |
Dear ChristopherD, Thank you for your reply . My MMC card don't contain any USER PROGRAM. I have cleared all Data from MMC card then Extract Firmware File to MMC card using PG. then inserted this MMC card in Controller . But On my controller i am getting following LED status: DC 5V: Green Continuos STOPU & STOP: Yellow Flickering BUS1F & BUS2F: yellow flickering As per Manual Meaning of these LED Status:: The following actions may be required to rectify the fault: Power OFF/ON Check micro memory card New commissioning procedure Replacement of SIMOTION C So Is there problem in MMC 0r IN Controller???? |
7/11/2015 1:36 PM | |
Joined: 5/12/2006 Last visit: 5/14/2024 Posts: 22251 Rating: (2985)
|
Hello,
ok then the boot up from the MMC works and i locks like a defect in the controller.
Christoph |