You can see the procedure for Absolute encoder adjustment at Chapter 11.2 of Manual: Function blocks to control the SINAMICS with SIMATIC S7 in TIA-Portal, at link: https://support.industry.siemens.com/cs/us/en/view/109475044 |
Last edited by: Alan S at: 04/26/2019 12:28:40 |
|
This contribution was helpful to2 thankful Users |
4/26/2019 12:29 PM | |
Joined: 10/11/2006 Last visit: 9/30/2024 Posts: 5909 Rating: (806)
|
Hello Jeroen, the mode 5 of SINA_POS is only for the function "set reference point". This reference point will not be available after a power on. You have to do an absolute encoder adjustement to store it. There is a SIMATIC block available for the abs encoder adjustement, please have a look at the following SIOS entry: https://support.industry.siemens.com/cs/ww/en/view/109760317 I hope that helps you! |