1/18/2022 4:51 PM | |
Joined: 9/27/2006 Last visit: 9/22/2024 Posts: 12282 Rating: (2684) |
Hello Shahab; My experience with S7-Graph has been with Simatic Manager and S7-300 PLCs, so I can onlly provide what I remember, and point you to the S7-Graph v5.3 manual: https://support.industry.siemens.com/cs/ww/en/view/1137630 One of the standard actions in S7-Graph is "Call", which will open a specified FC, FB, SFC or SFB. FBs and SFBs must have a generated IDB, which you can open by double-clicking on the FB Call. To negate a signal in S7-Graph, if i remember well, must e done in a FBD network, not LAD. It is easy enough to enter a FBD network, look it up in the manual. Hope this helps, Daniel Chartier |
Last edited by: dchartier at: 01/18/2022 16:52:21 |
|
1/19/2022 3:20 AM | |
Joined: 12/8/2016 Last visit: 9/17/2024 Posts: 86 Rating: (0) |
Hello Daniel, thank you so much for your response. it is possible to invert a signal in STL too when i insert an action and write a command like attached picture according to the manual, but please see the second page, i want to invert one of the input of inside FB, i didnt find solution, please check again. Best regards. Attachmentinvert address.pdf (574 Downloads) |