12/15/2014 8:13 AM | |
Joined: 1/21/2013 Last visit: 10/8/2024 Posts: 4620 Rating: (708) |
Hello Muhammad Awais Faiz, Look above |
Last edited by: Ste39 at: 12/15/2014 8:18 AMLast edited by: Ste39 at: 12/15/2014 8:15 AM |
|
12/15/2014 8:32 AM | |
Joined: 10/7/2005 Last visit: 10/14/2024 Posts: 3024 Rating: (1054)
|
Only one minor correction to the above: S5 "DW14" becomes S7 "DBW28" (all DB addresses double when converting to S7). And personally, I would remove "A DB10" and change "L DBW28" to "L DB10.DBW28" to make use of S7's complete addressing mechanims. |
Cheers |
|
This contribution was helpful to4 thankful Users |
12/15/2014 8:43 AM | |
Posts: 12 Rating: (0) |
Thanks Mr.Ste39for solving my problem :) |
12/15/2014 8:47 AM | |
Posts: 12 Rating: (0) |
Thanks Mr.Marcjanfor your detailed help :) |
12/15/2014 8:48 AM | |
Posts: 12 Rating: (0) |
Yes Mr.fritzthis db10.dbw28 in S7 thanks alot |
Last edited by: Muhammad Awais Faiz at: 12/15/2014 8:49 AM |
|
This contribution was helpful to1 thankful Users |