Industry Online Support
Technical Forum
3/14/2011 1:21 PM | |
Posts: 316 Rating: (37) |
Hi, do you have a peripheral devices on your PG? What error and error message appears in the PLC? |
3/14/2011 3:56 PM | |
Posts: 62 Rating: (2) |
Hi Chilly_Garfield, Now, there's no actual hardware connect to PG. With the actual hardware, when download to CPU there's no error message. It's just when change hardware configuration, and try to download in run mode, CPU went to stop mode. So i try to reconfigure again and test with PLCSIM. Because at this moment the actual hardware is not available. Same problem is also with PLCSIM, there's no error message. PLCSIM's CPU go to stop when download hardware configure. I just wonder if CiR can test with PLCSIM. Thanks |
3/14/2011 4:52 PM | |
Posts: 316 Rating: (37) |
Hey yuwanee, i have test this situation with a PLC and a CiR object in PLCSIM. My PLCSIM V5.4 SP4have no problem. When I insert OB80 I can add new slaves without a failure. I think you have a other problem. E.g. Slave engineered, a failure in your programm or sth. other. What saies the diagnostic buffer? |
Last edited by: Chilly_Garfield at: 3/14/2011 4:57 PM |
|
3/14/2011 5:26 PM | |
Posts: 62 Rating: (2) |
Thanks Chilly_Garfield. The problem is i didn't download OB80. ^^ Thanks again. |