There is a CPU 314 IFM (314-5AE02-0AB0), it added the CP (6GK7 343-1CX10-0XE0). After loading the configuration in the PLC, the CPU is OK (no SF light is on), and the CP is not OK (SF indicator is on). Can I use this CPU and CP together? There is a document in which it is indicated that sharing is not possible. Although you can add a module to HW Config.
AttachmentFiles.zip (108 Downloads) |
Last edited by: Jen_Moderator at: 10/26/2017 7:10:39 AMAdded all files as an attachment. |
|
10/25/2017 1:28 PM | |
Posts: 3093 Rating:
|
Hello AlexEpro, Regards, |
10/25/2017 2:13 PM | |
Joined: 5/12/2015 Last visit: 11/2/2024 Posts: 6 Rating:
|
The CP diagnostic buffer is not available, because "Module not available" |
10/25/2017 2:57 PM | |
Joined: 7/9/2015 Last visit: 3/17/2025 Posts: 4200 Rating:
|
Hi, I think you can´t use this CP in this PLC because it´s not compatible. Please check manual of your CP - on page 22 there is listet a CPU 314 IFM with MLFB -5AE03- which is compatible. Your CPU is -5AE02- its older than -5AE03- and it´s not listed - so it´s not compatible. SIMATIC NET S7-300 - Industrial Ethernet / PROFINET CP 343-1 Lean Manual Part BRegards, Towome |
|
|