3/31/2014 10:10 AM | |
Joined: 10/11/2006 Last visit: 2/3/2023 Posts: 5412 Rating:
|
Hello, Using a three-winding transformer for the master and slave infeeds. In this case, only the neutral point of one winding may be grounded to prevent further electrical coupling viaground. |
Last edited by: TechTeam at: 3/31/2014 10:11 AMLast edited by: TechTeam at: 3/31/2014 10:11 AMWith best regards, |
|
This contribution was helpful to
1 thankful Users |
4/1/2014 3:34 AM | |
Posts: 4 Rating:
|
Thank you so much! In 12 - pulse mode, can the infeed in regenarative mode ? Best regards, konthup@ |
Last edited by: konthup at: 4/1/2014 3:34 AM |
|
Follow us on