Hello, Using a three-winding transformer for the master and slave infeeds. In this case, only the neutral point of one winding may be grounded to prevent further electrical coupling viaground. |
Last edited by: TechTeam at: 3/31/2014 10:11 AMLast edited by: TechTeam at: 3/31/2014 10:11 AMWith best regards, |
|
This contribution was helpful to1 thankful Users |
4/1/2014 3:34 AM | |
Posts: 4 Rating: (0) |
Thank you so much! In 12 - pulse mode, can the infeed in regenarative mode ? Best regards, konthup@ |