11/18/2016 12:29 PM | |
Joined: 5/12/2006 Last visit: 4/26/2024 Posts: 22231 Rating: (2980) |
Hello, yes i'm sure. The PROFINET IO-Controller is implemented in V2.0 of the S7-1200 FW. With V1.0 no IO-System can be created an the PN/IE Interface of the S7-1200 doesn't support IO-Controller! IP Assign: If a project loaded on the S7-1200? You must delete the user data on the PLC to assig the IP or load a project with the new configured IP Adress.
Christoph |
This contribution was helpful to1 thankful Users |
11/18/2016 2:37 PM | |
Posts: 72 Rating: (1) |
OK, I understand that S7 1200 works correctly with every Siemens's SD cards or it works only with dedicated to S7 1200 cards? |
11/21/2016 2:33 PM | |
Posts: 72 Rating: (1) |
yes, I have checked it's OK. Please see attachment |
11/21/2016 2:40 PM | |
Joined: 5/12/2006 Last visit: 4/26/2024 Posts: 22231 Rating: (2980) |
Hi, ok what say the diagnostic buffer of the PLC ? Any Error logged? Regards Christoph |
11/21/2016 2:40 PM | |
Posts: 72 Rating: (1) |
I dont know why it isnt assigned... :( |
11/21/2016 2:46 PM | |
Joined: 5/12/2006 Last visit: 4/26/2024 Posts: 22231 Rating: (2980) |
what you mean? |
11/21/2016 2:49 PM | |
Posts: 72 Rating: (1) |
I refered to that communique: "At least one component not assigned to a drive object' |
11/21/2016 4:00 PM | |
Joined: 5/12/2006 Last visit: 4/26/2024 Posts: 22231 Rating: (2980) |
and which motor you use? What is connected to the DQ Port of the G120? |