Dear BramRondele, It's strange for me your situation. It's normal the warning message "Going online: the HW configuration of the HMI_RT_1 was changed but it was not compiled and loaded yet. The shown diagnostics is possibly inconsistent or wrong." when your panel goes online. I don't think there is something to do with the Type of the
PG/PC interface, if you are using Ethernet to connect to your panel, the PN/IE
(Profinet/Industrial Ethernet) is the right selection. What you should configure is the Network Adapter's setting (IP adddress, Subnet mask, Default gateway, etc). If your PC can connect with your panel directly, it should be able to connect via your plant network also, unless there is something to deal with the plant network, ex. the plant network's topology or the plant network is managed by an IT department. If this is the case, you should check with the IT expert. You can also use the PRONETA tool to scan your plant network making sure that your devices' network settings are all correct. If your PC can catch the device with PRONETA, normally it should be able to connect with it also.
The latest version of PRONETA can be downloaded from the below link: PRONETA 2.5.0.27 Commissioning and Diagnostics Tool forPROFINET Best regards, Yu-wen |