Hi all, I have CPU 1516F and OPC UA Server on a PC. Is it possible to make the PLC a client of the UPC UA? |
5/31/2018 3:09 PM | |
Joined: 9/27/2006 Last visit: 3/17/2025 Posts: 12344 Rating:
|
Hello; A S7-1500 CPU can only act as a OPC UA server. This is shown in the Technical data of the repsective CPUs; see the screenshot below. An interesting alternative is the OPC UA client (in C#/.NET) proposed by Siemens, based on the OPC UA libraries from OPC Foundation. It would allow a configured PC to connect to a number of S7-1500 OPC UA servers over TCP/IP to collect the required data. OPC UA client for the S7-1500 OPC UA server : https://support.industry.siemens.com/cs/ww/en/view/109737901 Hope this helps, Daniel Chartier |
6/4/2018 1:04 PM | |
Posts: 3 Rating:
|
Hi dchartier, Thanks for the info i hoped that there is some other way to make the PLC client. |
11/26/2019 12:50 PM | |
Joined: 9/9/2014 Last visit: 2/12/2025 Posts: 246 Rating:
|
Hello, Murof, Currently, the OPC UA Client is supported in the TIA Portal version 15.1 TIP: S7-1500 OPC UA Server Client communication, exporting XML files I checked (it is really available) |
Best Regards |
|
This contribution was helpful to
4 thankful Users |
11/27/2019 3:39 PM | |
Joined: 8/3/2009 Last visit: 3/18/2025 Posts: 15003 Rating:
|
Hello Unreality Yes of course it its available now in V15.1 (and of course also in V16) but my last post was in 6/7/2018. But thanx for your Information in this Topic! Bye Murof |
If this Information really helps, you could use the Rate function |
|