Dear All! I can't connect with a siemens s7-300 plc with simatic s7 pc adapter usb a2 Error 0x031a: No active PROFIBUS/MPI network found. If you want the CP of this PC to be the only active module (for example in DP master mode), the setting <PG/PC is the only master on bus> must be activated. I tried to change the master on the bus, after that
Attachmenterror.rar (119 Downloads) |
7/22/2015 11:16 AM | |
Posts: 8 Rating:
|
New PLC CPU313i 313-5BG04-0AB0 1x MPI |
7/22/2015 2:05 PM | |
Joined: 3/5/2014 Last visit: 8/5/2022 Posts: 5521 Rating:
|
hi metrobijs, try to set the CPU to delivery state. Then you know the communication parameters. See how it works in following manual. Also the Properties of the CPU in the delivery state are provided in the manual. Chapter 9.5 page 197: SIMATIC S7-300 CPU 31xC and CPU 31x: InstallationAfter doing this you can be sure to have these communication settings and try with suitable settings of your Adapter.hope this helps,regards, |