1/2/2021 4:50 PM | |
Joined: 9/21/2012 Last visit: 10/1/2023 Posts: 3778 Rating:
I would start by investigating PLC's diagnostics buffer, to see the cause of the faults. |
1/4/2021 3:49 PM | |
Joined: 7/7/2010 Last visit: 9/29/2023 Posts: 13751 Rating:
Use the online TIA Selection Tool ( TIA Selection Tool | Totally Integrated Automation (TIA) | Siemens Global ) and populate the PLC rack with your exact components. It will suggest a power module (PM) to be placed somewhere in the midst of all that IO to provide enough power for the communications BUS.
science guy |
This contribution was helpful to
1 thankful Users |
1/5/2021 12:37 AM | |
Posts: 2 Rating:
Yes, I was able to figure out the issue last week. I placed a system power supply in the beginning of the bus on the TIA Selection Tool and it worked. Thank you!