4/22/2016 2:06 AM | |
Posts: 4 Rating:
|
I have a Lenovo Z40 Core i7 8 GB Ram, with Windows 7 Professional SP1 and TIA Portal V12 SP1 Updt 5 and v13 SP1 Upd 5 (now Upd 8). I tried to do this on both adaptors, Realtek PCIe GBE and Intel(R) Dual Band Wireless-AC 3160 but no one worked.
------------------------------------------------------------------------------------------ |
Last edited by: Min_Moderator at: 4/22/2016 12:24:46 PMNew subject after splitting |
|
4/22/2016 1:12 PM | |
Joined: 7/9/2015 Last visit: 3/27/2025 Posts: 4210 Rating:
|
Hi, if you have problems with PN components you can also check if PROFINET IO RT protocol is installed and enabled. Please check this FAQ: https://support.industry.siemens.com/cs/de/en/view/23585653 Regards, Towome |
|
|
5/31/2016 6:31 PM | |
Posts: 1 Rating:
|
I have to spend 10 hours to solve same problem that happend to me. However it am very glad to to share my experience here altough i believe the source of problem for this not only one. After trying so many advices, finnaly I turned my focus on symantec end point protection, i found the data send via utp to S7 1200 CPU was bloked by symantec firewall. I just disabled it and finnaly i could connect my laptop to CPU. I attached here the print screen of the evidence. AttachmentSymantec End Point.pdf (653 Downloads) |
This contribution was helpful to
1 thankful Users |