Hello everyone I need help I have S7-1200 CPU 1215 and ET200SP with TM Count 1×24 I connected an encoder and I see the value But I can't reset it The value is reset only after turning off the power How can I reset it through the software? Thanks ------------------------------------------------------------------------------------------ |
Last edited by: Jen_Moderator at: 08/18/2022 10:41:38New subject after splitting |
|
8/18/2022 9:39 AM | |
Joined: 6/19/2019 Last visit: 3/18/2025 Posts: 711 Rating:
|
Hello let see this VIDEO about at 25:30 you will see then entered "High_Speed_Counter_1''.CurStartValue 50 and trigered "High_Speed_Counter_1''.UserCmdFlag.SetDQ0 to true it will count from start value so if you enter start value 0 and you will trigger "High_Speed_Counter_1''.UserCmdFlag.SetDQ0 you will be start counting from 0 again |