5/14/2017 6:51 PM | |
Posts: 2826 Rating: (684) |
Hello Walter. You will have to grow a thicker skin (not meant literally). There is nothing wrong with your image - it is clear and to the point. >>>>>>>>>>>>>>>>>>>>>>>>>>>>>>>>>>>>> Why do you think you need 6 signals? Each phase uses x1 signal: either (+) or (-) of the phase. UNLESS you have differential signals. In that case you need a converter to convert to 24Vdc level the PLC can understand. Make sure what type signal you are getting: 24V, 5V, NPN (open collector), PNP or differential. ABZ encoder should can use x3 signals not 6. you select if the phase is (+) or (-). In most of my cases I do not use the Z phase. Most times are AB, but many are even only A phase. >>>>>>>>>>>>>>>>>>>>>>>>>>>>>>>>>>>>> Making the PLC responsible for being the electronic gearbox between AC motor and servo is not a good idea. The PLC is slow. Unless quick reaction is not something you need. My cases have the analog output of the AC motor connected to the analog input of the servo motor. With digital signals you can select that the servo uses its own analog input as speed setpoint or use pulsing from the PLC. You can even have a relay select between analog from AC drive or PLC to go to the servo. A digital input on the PLC can select to "freeze" the speed while the relay is switching (20ms time). >>>>>>>>>>>>>>>>>>>>>>>>>>>>>>>>>>>>> Ignoring my previous idea: For calculating the "speed" of the AC motor you can use PERIOD mode. There is an example on how to use PERIOD mode. Look at: LINK.
|
5/15/2017 2:48 AM | |
Joined: 4/26/2017 Last visit: 4/9/2024 Posts: 65 Rating: (1) |
i am sure that the encoder power supply is +24VDC. And the output is the common one: in quadrature. I am almost sure those two encoders will works as spected.
|
This contribution was helpful to1 thankful Users |
5/17/2017 8:02 PM | |
Joined: 4/26/2017 Last visit: 4/9/2024 Posts: 65 Rating: (1) |
Mr. Dan
|
5/17/2017 10:11 PM | |
Posts: 2826 Rating: (684) |
Hello Walter, you should be able to do what you want to do. But now we both have a problem: Perhaps look at all the configuration settings - make sure there are no "gating" mechanisms blocking operation. Do mention next time how you are using the HSC. For "period" measurement, for example, %ID1000 does not work. "period"measurement also has a maximum value it can measure - perhaps around 2sec.
|