Hello, it is only possible via GSD file. https://support.industry.siemens.com/cs/ww/en/view/105644659 GSD file doesn't support Tel.105, so no DSC is possible. |
With best regards, |
|
1/21/2021 3:35 PM | |
Joined: 1/17/2013 Last visit: 4/23/2025 Posts: 1112 Rating:
|
Dear Technology Team, Which telegram is can use ? How to wiring control and power apart of D425-2DP/PN ? Best Regards, Vorapob |
Best Regards, |
|
1/22/2021 10:35 AM | |
Joined: 10/11/2006 Last visit: 4/24/2025 Posts: 6009 Rating:
|
Hello, you can use TEL: 102. You need a Profinet V90. Connection V90 to D435 is via Profinet. Power and 24V wiring is like described in manual.. D435_2 https://support.industry.siemens.com/cs/ww/en/view/109757331 V90 https://support.industry.siemens.com/cs/ww/en/view/109780069 |