5/11/2011 2:34 PM | |
Posts: 51 Rating:
Hello! Can you have the AS-interfaeand 24V aux in the same cable? If so, can you use any round4x1,5mm2-cable? /Pontus |
5/11/2011 3:06 PM | |
Joined: 9/27/2006 Last visit: 3/23/2025 Posts: 12344 Rating:
Hello Pontus; As-i uses a 30V DC power supply to transmit both power andtransmission. (as a digital overlay on the power signal). This power is generally within the specs of a 24 V circuit. See the www.as-interface.com website for more information (look for the As-i Academy section for details on the bus specifications). Although the use of the flat As-i cable is recommended, many manufacturers (Weidmuller, Schneider, Siemens) offer As-i modules with screw terminals for connection of As-i power ansd signal. Look at the Products section of the As-i link shown before, or in this Siemens As-i System manual: http://support.automation.siemens.com/WW/view/en/26250840 Hope this helps, Daniel Chartier |
5/17/2011 1:10 PM | |
Joined: 1/26/2006 Last visit: 9/2/2024 Posts: 6 Rating:
Have done exactly this many times with zero problems. |