Hi, Some PID parameters are not overwrite by donwload. Alternatives: reset the CPU to factory settings, create a new instance DB for the same PID applications, set the values from Watch table. About PID parameters (gain, TI, TD), I suggest you change it by watch table. Takea look at /tf/WW/en/Posts/33957#top to get the addresses. |