6/23/2010 6:22 AM | |
Posts: 12 Rating:
|
Yes, i'm using P_RCV FB.Status and error codes are the same: null. |
6/23/2010 9:51 AM | |
Posts: 3093 Rating:
|
Hallo Andrius, how did you setup the cable? Are the pins of the communicatio partner named R(A) or R-? R(A) of CP340 is equal to R-. Regards, Kaulquappe |
6/23/2010 10:47 AM | |
Posts: 12 Rating:
|
Hello, I connect device's RS485 contact A to CP340 pin 4 and device's contact Bto pin 11.No connection GND between device and CP340.
|
6/23/2010 10:49 AM | |
Posts: 12 Rating:
|
I use CAT5 UTP cable. |
6/23/2010 10:55 AM | |
Posts: 3093 Rating:
|
Hello Andrius, is contact B of the device + or -? You must connect - to - and + to +. Regards, Kaulquappe |