10/27/2009 10:16 AM | |
Posts: 41 Rating: (0) |
Hello, I am having trouble forcing S7 1200 tags.It seems that forcing is disabled for some reason that I couldn't find. (see screenshot). Your help please! BR |
10/27/2009 10:52 AM | |
Posts: 12 Rating: (1) |
You can only force PIW and PQW not induvidual bool |
10/27/2009 11:09 AM | |
Posts: 41 Rating: (0) |
Thanks a lot PLC_GURU, it worked for me. But why is it only possible to force Peripheral IO? (maybe because of the first releease?) |
10/28/2009 2:05 AM | |
Joined: 10/7/2005 Last visit: 5/14/2024 Posts: 3005 Rating: (1048) |
Not quite true, you can force indivudual inputs and Outputs too. What you have to do though is to add ":P" to the I/O address which "declares it as a peripheral (e.g. Q0.0:P or I0.0:P). The reason for why you have to do this shall forever and day only be known to the same "genius" that decided NOT to have STL available in a 1200. The good news with the "I/O Watchtable" is though that you can "auto complete" it by entering one address andthen dragging it down (which helps with commissioning if you have a number of I's and Q's to force as it saves you from having to add :P to each and every one of them) I hope this helps |
Last edited by: fritz at: 10/28/2009 2:08 AMfixed typos Cheers |
|
This contribution was helpful to1 thankful Users |
10/28/2009 4:52 AM | |
Posts: 41 Rating: (0) |
Many thanks |
10/29/2009 3:01 PM | |
Posts: 4 Rating: (0) |
Ciao,I have tested to force Output without :P and it functions too.I have T.I.A. Portal 10.5 SP1.See attachment Do you have the same version ? |
10/6/2010 2:10 PM | |
Joined: 8/28/2009 Last visit: 2/23/2024 Posts: 1 Rating: (0) |
Hey, if you have software STEP 7 Basic + SP2, you can force a single variable bit |
11/11/2014 5:12 AM | |
Posts: 5 Rating: (0) |
It's work for Input and Output thank you very much
|
7/3/2018 4:12 PM | |
Joined: 4/7/2018 Last visit: 10/26/2023 Posts: 4 Rating: (0) |
Hi, Can you help me please???? :( |