DearPittiplatsch, i am using IM 151-8 pn/dp cpu with firmware v 3.2 and when i config i device in one of the cpu and create its gsd file which is used in master system as per attached file. there is no fault on the both cpu but with using load transfer function 1 m not be able to transfer the data. i m using dprd_dat(sfc14 and 15) for data transfer but it dont help us. one more problem if i m not using ob122 then one of the cpu gose into stop mode. AttachmentI DEVICE.zip (66 Downloads) |
Last edited by: O_Moderator at: 9/16/2014 10:43 AMLast edited by: shivendra jaiswal at: 9/16/2014 7:50 AMshivendra kumar jaiswal |
|
9/16/2014 9:46 AM | |
Posts: 1368 Rating:
|
Hello, what error/Ret_Val value you get with the SFC? Is the LADDR correct? The transferarea between Controller and I-Device? Here https://www.automation.siemens.com/mdm/default.aspx?DocVersionId=63972520715&Language=de-DE&TopicId=62572430859 you find an example with PROFIBUS (but it is similar to PROFINET) |
9/16/2014 11:39 AM | |
Joined: 9/2/2012 Last visit: 2/27/2023 Posts: 15 Rating:
|
Dear https://www.automation.siemens.com/mdm/default.aspx?DocVersionId=22512940939&TopicId=22162162699 |
shivendra kumar jaiswal |
|
9/16/2014 12:02 PM | |
Posts: 1368 Rating:
|
Hello, that right. You do not need any blocks, because you configure a transfer area between Controller and Device you have access (process image). If you do not or cannot place the data in a process image, then you should use the system functions SFC14 and SFC15 for data communications. FAQ: http://support.automation.siemens.com/WW/view/de/21848242 And example for I-Device you find in the link, you posted https://www.automation.siemens.com/mdm/default.aspx?DocVersionId=22512940939&Language=en-US&TopicId=22162162699 |