Hello, The IM151-1 is a Profibus DP slave. The CB1241 and/OR CB1241 may have a RS458 interface, but do not support Profibus DP protocol. What you need is Profibus DP Master. The correct module for that is the CM1243-5 http://support.automation.siemens.com/WW/view/en/42131407 The configuration is done in TIA portal, and the I/O modules plugged behind the IM151 will beaccessible directly in the process image of the PLC, just like central periphery. |