7/2/2013 9:11 AM | |
Posts: 12 Rating: (0) |
Dear Colleague’s, Can anyone from you worked before with absolute encoder CEV65. Unfortunately I should have to prepare some block to working with this encoder but 1. First off all I do not have any experience with this device, 2. Second I do not get from master project any sample for this, From the specification which I found on the internet website I get it data which I show below: Data Resolutions: 4096 (resolution is saving in 12 bites) Revolutions: 4096 Encoder is in Network Profinet Encoder has four input byte
Task I would like take data from encoder (high of table) and check if the value is correct (comparison with internal encoder) S7 400 Configuration hardware of encoder you can find at enclosed. According to the documentation I use SFB53 to reading data from this encoder. I am not sure if this block is okela for this.. Request to everybody If anyone from Users of this forum has same sample and would like to show this same sample solution I would be very appreciate. Best regards AttachmentCfg.pdf (109 Downloads) |
7/17/2013 7:42 PM | |
Posts: 691 Rating: (36) |
hi SFB53 and SFB 52 will serve your application.for sample programe you can go to simatic library regards |
8/6/2013 7:59 PM | |
Posts: 12 Rating: (0) |
Hello Everybody, I found solution and should be usefully I hope for every user of the forums… Part of My function I add at enclosed. P.S Encoder is Multiturn, and I use SFB 53 for preset Topic is close, best regards… AttachmentCEV.pdf.pdf (98 Downloads) |
This contribution was helpful to1 thankful Users |
3/4/2014 7:20 AM | |
Posts: 1 Rating: (0) |
DearMrMasterMaths, Could you upload to this forum the example program this profinet encoder? thank U AM
|