7/15/2018 7:45 PM | |
Joined: 12/7/2011 Last visit: 3/3/2023 Posts: 375 Rating:
|
Hi to all. I have a multiproject with three S7 400 FH System. On each one, there is a safety software, all of them are completely the same. But in only one of them, after the compilation, i get 200 errore in the concistency tab. the error is: E: Unauthorized interconnection of the F-parameter 'F_Logic_Burner_3\318_2\OUT' between shutdown groups 'F_AnalogInput' and 'F_Logic_Burner_3' [Remedy 2: Always use communication blocks F_S_R, F_R_R or F_S_BO, F_R_BO for interconnection between the shutdown groups]. I dont understand why i get this error, because the description its a little bit confused, Furthermore, when i select this error, and i go to the chart, it show me the block who generate it. I've already tryed to delete all the involved blocks, but after the compilation, i got again the same error. How can i delete it? What can i check? Thanks to all. Regards. Duccio. Attachmentblocks.pdf (67 Downloads) |
Last edited by: Duccio at: 7/15/2018 7:45:23 PM |
|
7/18/2018 7:53 PM | |
Joined: 12/7/2011 Last visit: 3/3/2023 Posts: 375 Rating:
|
Hi hd, Thanks for your reply, i've tryed to put all under the same F-Group, but the result doesnt change. The strange things is that in the other project, the F-Group configuration is tha same, but only in this i get the error. Attachmentcfc.pdf (75 Downloads) |
7/19/2018 10:28 AM | |
Joined: 12/7/2011 Last visit: 3/3/2023 Posts: 375 Rating:
|
Hi hd, I think i got the problem, but i dont know how can i solve it. I told you that i have two project completely the same, but one with a consistency problem, and the other no. Now i found out that the project with the problem, the blocks are executed in a not F-Group. How can i change the execution folder to an F-Group? Thanks Duccio. AttachmentRun Sequence.pdf (74 Downloads) |
Follow us on