4/2/2016 3:55 PM | |
Posts: 1 Rating:
Is there a way to also change the SIMOCODE current configuration settings using a Comfort HMI panel that is a OPC-UA client connected to the SIMOCODE which is a OPC-UA server i.e. there is no PLC? ------------------------------------------------------------------------------------------ |
Last edited by: Min_Moderator at: 4/4/2016 3:07:58 PMNew subject after splitting |
4/3/2016 6:46 AM | |
Joined: 4/23/2010 Last visit: 11/23/2024 Posts: 8092 Rating:
This link may help you. |
4/4/2016 4:28 PM | |
Joined: 5/17/2010 Last visit: 12/7/2024 Posts: 226 Rating:
Hi, At the SIMOCODE pro V PN System Manual you can find a table of all available OPC UA variables at chapter 16.2. There is no variable for set current listed. It's necessary to write a Data Record 130 by acylic data exchange. D-WORD 80.0 includes the Set Current Is1. I don't know if this is possible with the HMI communication channel, if not a PLC is required for this to change this Parameter. The SIMOCODE Operator Panel with Display supports parameter changes for Set Current (see System Manual page 74). Download: System Manual SIMOCODE pro PROFINET 10/2015 Kind Regards |