3/10/2025 9:26 AM | |
Joined: 7/5/2013 Last visit: 4/28/2025 Posts: 3153 Rating:
|
Hi, you could use job mailbox order 51 to change a screen from PLC. Following is for TIA 14, but should be the same for TIA 17: "Job mailbox" area pointer (Basic Panels, Panels, Comfort Panels, RT Advanced) Regards, Frink |
Pi is exactly three! |
|
3/12/2025 10:29 AM | |
Joined: 8/3/2009 Last visit: 4/28/2025 Posts: 15368 Rating:
|
Hello In this FAQ there are a few examples: https://support.industry.siemens.com/cs/ww/en/view/93909293 Unfortunately Basic Panels cannot use VB Scripts, so you cannot check if the triggertag is 1 or 0 (so if its rising or falling edge). you could use an additional network in PLC and use the Screen number and an integer for calling the Screen. if the Screennumber in this tag changes you use at event screenchange the systemfunction ActivateScreenByNumber Bye Murof |