Hi İxo65, Two LOGO! I'm asking about changing the counter value between two logo. Is it possible to do this without using ''access tool''? Is there other method for transfer values between LOGO? I can do this by network analog output but this time value stays at 32767. I want to count to 500000 The program is attached. ------------------------------------------------------------------------------------------ Attachment8 sıralı Pnomatik ekm.zip (57 Downloads) |
Last edited by: Jen_Moderator at: 05/05/2020 14:30:48New subject after splitting |
|
5/5/2020 4:51 PM | |
Joined: 12/18/2014 Last visit: 12/5/2023 Posts: 31546 Rating:
|
I did another test. I rejected the option first because it doesn't work in the simulation. Then I tested it with 2 real LOGO!s and it worked. You can transfer a counter value greater than 32,767 (maximum 999,999) to another LOGO! and displayed there by using of another counter. AttachmentCounter_value_from_a_LOGO!_to a_another_LOGO!_0BA8.Standard.zip (92 Downloads) |
5/6/2020 12:43 PM | |
Joined: 5/2/2019 Last visit: 11/28/2023 Posts: 35 Rating:
|
Dear ixo, Thank you very much for your solution. I have tried and it works perfectly. But I couldn't do that in my work. I think I'm making a mistake. B005 ... B008 does not work. Can you help me? Attachment8 unit drill.zip (41 Downloads) |
5/6/2020 2:01 PM | |
Joined: 12/18/2014 Last visit: 12/5/2023 Posts: 31546 Rating:
|
You must also the V-words (VW0, VW4, VW8 and VW12) to the other LOGO!. I made it for you. See attachment. Attachment8 unit drill_V2.zip (86 Downloads) |