Hello.... is there any way to close/open brake on V90 controlled motor using s7-1200 /newest fw/ and telegram 3???.......I mean open/close uncondicionally,not with enable MC_power....in telegram 3 mapping there is tag named "OpenHoldingBrake" /STW1/.....but this bit has no effect in V90...... thans a lot... --------------------- |
Last edited by: CS Moderator at: 06/17/2021 09:02:06new subject after splitting |
|
6/22/2021 1:43 PM | |
Joined: 10/11/2006 Last visit: 3/13/2025 Posts: 5997 Rating:
|
Hello, you have to copy statusword and encodervalue from Tel 102 to Tel 3 in MC_Preservo and control word and setpoint from Tel 3 to Tel 102 in MC_Postservo. It is not necessary to provide the additional words of Tel.102. For Tel.3 you have to do a datablock like described in chapter 4.2.3 Datablock "EncoderTel81" Instead of PD_Tel81 use Data type PD_Tel3. Using the MC-PreServo and MC-PostServo organization blocks https://support.industry.siemens.com/cs/de/en/view/109741575 |
With best regards, |
|
6/23/2021 1:59 PM | |
Joined: 10/11/2006 Last visit: 3/13/2025 Posts: 5997 Rating:
|
Hello, yes, Tel3 includes drive and encoder. Tel 750 is possible , but S71200 TO doesn't support it. So you have to do it applicative. The default in Tel. 750 = 0%, so the limits in the V90 will be 0%. I would recommend S7-1500. With S7-1200 V90 with Basic Positioner and FB 284 is an option. https://support.industry.siemens.com/cs/ww/en/view/109747750 |
With best regards, |
|