Hello vipz; A GSD file is required to introduce a Profibus-DP slave in a master,s profibus configuration; a GSDML file does the same for a Profinet system. As-i works in a very different way, as you can see if you look at your As-i master documentation, and does not use GSD files for slave identification. Manual AS-i Master CM 1243-2 and AS-i Data Decoupling Unit DCM 1271 for SIMATIC S7-1200 https://support.industry.siemens.com/cs/fr/en/view/57358958 Most of the data transmitted over As-i is digital (binary inputs and outputs). Wgen you want ot use it to read/write analog values (as in the case of a DTA100, you have to use SFB52/53 to read and write data records, in your program; see the following extract ofrom the manual cited above): Calls The following blocks are used for reading and writing data records: Table: Blocks for reading and writing data records
You will find these blocks in STEP 7 in the operations list under "Advanced operations, distributed I/O" . Here is a copy of an similar answer that was provided on another forum, a few years ago, with some details that could help you (take into account that the thrad considered a S7-300 As-i master) : http://www.plctalk.net/qanda/showthread.php?t=37240 Hope this helps, |
||||||
This contribution was helpful to
1 thankful Users |
8/12/2016 10:46 PM | |
Joined: 9/27/2006 Last visit: 3/22/2025 Posts: 12344 Rating:
|
Hello Vipz; When the manual of the Siemens As-i masters (like your CM 1243-2) discusses the configuration of the As-I slaves, it means that either you can try settong them up as you have, or you can configure them directly oin the HWCopnfiguration editor. See this from the CM 1243-2 maniual: Access without configuration of the AS-i slaves with STEP 7 If you have not configured the AS-i slaves in STEP 7, you can access the AS-i digital values via the I/O area of the SIMATIC. In this case STEP 7 automatically activates the "System assignment" parameter which causes a 62 byte long I/O area to be reserved in the SIMATIC.STEP 7 basic configuration (Page 38) Transferring AS-i analog values You can access analog data of an AS-i slave via cyclic services if you have configured this AS-i slave in STEP 7 as an analog slave (see section "Configuring AS-i slaves (Page 40)"). If you are not configuring any analog slaves, you can only access the data of the AS-i slave via the acyclic functions (see section "Accessing AS-i analog data via acyclic services (Page 52)"). I suggest you have a look at this sample program provided by IFM for a CP 343-2 As-i master (on a S7-300 CPU). You should be able to follow the steps even with TIA Portal. Please remember the example uses S7-300 SFCs, you need SFB52/53 in your project. Look for this entry: Program sample Step7 CP343 ASI Master with RFID DTS125 In the followingh link: https://www.ifm.com/download/read_webidsys_en Hope this helps, Daniel Chartier |
This contribution was helpful to
1 thankful Users |
10/14/2017 8:48 AM | |
Joined: 8/5/2017 Last visit: 3/28/2023 Posts: 2 Rating:
|
AttachmentCM1243-2 with IFM DTA100 TO write.docx (405 Downloads) |