1/14/2019 6:00 PM | |
Posts: 3093 Rating:
|
Which error does MB_Master report? |
This contribution was helpful to
1 thankful Users |
1/22/2019 9:40 AM | |
Posts: 114 Rating:
|
Can anybody please help me regarding this still I am struggling to find a solution. |
Last edited by: K C Das at: 1/22/2019 9:40:49 AM |
|
1/22/2019 2:42 PM | |
Posts: 3093 Rating:
|
You must evaluate the outputs in your program: How do you evaluate the status of system blocks in STEP 7 (TIA Portal)? |
This contribution was helpful to
1 thankful Users |
1/23/2019 6:36 AM | |
Posts: 114 Rating:
|
Hi, Thanks for the reply, but as I stated before that it is reporting error code 7002.which is not helping me to find out the exact details. my settings for COM Load is as following do you think any changes please suggest me Baudrate = 19200 Parity = none flow control = none databits = 8 stopbit = 1 |
1/23/2019 1:22 PM | |
Posts: 3093 Rating:
|
7002 is a status message which is reported with ERROR=FALSE. You need to know STATUS when ERROR=TRUE. |
This contribution was helpful to
1 thankful Users |