Hi Daniel, according to manual of CM1243-2 ASi Master you are using ASi slave specific command "Read AS-i slave ID string (Read_Identification_String)" with index 30dec ( Manual AS-i Master CM 1243-2 and AS-i Data Decoupling Unit DCM 1271 for SIMATIC S7-1200 ) Which firmware version of CM1243-2 and CPU1200 do you use? --> https://www.ifm.com/at/de/product/AC1402 Have you compared the ASi communication between the IFM ASi Master and the Siemens CM1243-2 ASi Master with e.g. an AS-i Analyzer / AS-i trace tool? If yes, could you maybe see an difference regarding the handling of the command "Read ID string"? kind regards |
2/20/2019 11:15 AM | |
Posts: 2 Rating:
|
Problem was solved with help of Siemens support. CM1243-2 have to be update to FW 1.1.25. |