If you want to connect a network input in the Logo via SMS, you have to remember that the CMR sets the input static. The SMS for switching on is:
The commands switches the VM bit V100.0 on and off. The choice of the VM-100 bytes is not mandatory, you can choose it freely. To switch a network input dynamically, you need a trick in the logo program. In attachment a small logo program, which shows you both options. AttachmentCircuit Diagram1.zip (224 Downloads) |
This contribution was helpful to1 thankful Users |
5/17/2016 4:24 PM | |
Joined: 12/18/2014 Last visit: 12/7/2024 Posts: 34362 Rating: (4281)
|
Do you have the variable declared in the CMR?
AttachmentLOGO! 8 - Industrial Ethernet LOGO! CMR2020 _ LOGO! CMR2040_side_86.pdf (236 Downloads) |
Last edited by: ixo65 at: 5/17/2016 4:31:22 PM |
|
5/17/2016 4:39 PM | |
Joined: 12/18/2014 Last visit: 12/7/2024 Posts: 34362 Rating: (4281)
|
Follow the link. It explains what you need to create everything, to perform an action with an SMS in the logo. Communication between two LOGO! Controllers by means of LOGO! CMR and SMS |
5/20/2016 7:39 AM | |
Posts: 5 Rating: (0) |
It's working perfectly now as we specified. Thanks for help! Best, |