9/9/2013 8:52 AM | |
Joined: 10/9/2007 Last visit: 9/18/2024 Posts: 1249 Rating: (115)
|
Hi John /xx is not firmware, but hardware revision. This is important between firmware and hardware. The "parameter set", which is the device driver installed in digsi, must be compatible with the firmware - not directly to the hardware, but indirectly as the firmware must be compatible with the hardware. Here you can find the compatibility table between HW, FW, parameter set and protocols: http://www.energy.siemens.com/ecc_pool/SIPROTEC4/f4a3eb42-011a-4f58-ae8b-d73b7bc0a7d8/Readme_fwup_04-13.pdf 1. A best practice is always to keep the Digsi file as backup and not rely on the device. This is mandatory for projects with IEC61850 and Profibus FMS, as not all information is stored in the device, such as GOOSE connections 2. check if the firmware in the device is compatible with the parameter set in digsi. If yes, just upload the file with "initialize device". Mike |
Energy Automation products: Sicam, Siprotec, Digsi |
|
9/19/2013 11:46 AM | |
Joined: 4/24/2009 Last visit: 8/20/2024 Posts: 2682 Rating: (135) |
New question was splitted to when in the display of siprotec appeared I1=0.28kA, offset 10 appeared 0002Hex. why it coming like that? Best regards O_Moderator |