6/30/2015 8:44 PM | |
Joined: 5/12/2006 Last visit: 4/26/2024 Posts: 22231 Rating: (2980)
|
Hello, you can commissioning the drive only in Starter and begin with this. If you have configured the communication telegrams in STARTER you can use the GSDML Generator to generate exactly this configuration as GSDML which can be installed in TIA, so you must not configure the telegrams in TIA. |
This contribution was helpful to1 thankful Users |
7/1/2015 8:28 PM | |
Joined: 5/12/2006 Last visit: 4/26/2024 Posts: 22231 Rating: (2980)
|
Hello, if you use safety with PROFISAFE you need a F-PLC (Safety PLC) which communicate with the Drive. This communication is done wite the PROFISafe telegramms like Tel 30 or Tel 31. The Safety PLC send the safety controlwords to the drive and read the status word from the drive with this telegrams, but only the safety data. To control the technology functions or motor you need a telegram like Tel 3 or Tel 111 to send the commands from the PLC to the Drive and read the status back. So you must configure 2 telegrams , one for the safety chanel and one for the drive control. in the application examlpes you can find more information: https://support.industry.siemens.com/cs/ww/en/view/82841762 https://support.industry.siemens.com/cs/ww/en/view/82526134 https://support.industry.siemens.com/cs/ww/en/view/68624711 Regards |
This contribution was helpful to3 thankful Users |
8/3/2017 9:32 PM | |
Joined: 7/25/2017 Last visit: 6/30/2021 Posts: 1 Rating: (0) |
Hello, I can't see the link. |
8/8/2017 8:01 AM | |
Joined: 5/12/2006 Last visit: 4/26/2024 Posts: 22231 Rating: (2980)
|
what you mean? |
Follow us on