4/29/2021 8:45 PM | ||
Joined: 2/25/2016 Last visit: 9/13/2024 Posts: 9 Rating: (0) |
I am trying to communicate Cu-320-pn-2 with s7-400 PLC. But I'm Not able to communicate i have attached photos of HW Configuration of STEP 7 (V 5.5 SP3) i Have Also Attached Photos of Starter (V5.4) - i have used the following GSDML File i used V2.25 ------------------------------------------------------------------------------------------ AttachmentPhotos.zip (153 Downloads) |
|
Last edited by: Jen_Moderator at: 04/30/2021 09:11:32New subject after splitting |
||
4/29/2021 9:43 PM | |
Joined: 2/25/2016 Last visit: 9/13/2024 Posts: 9 Rating: (0) |
s7 400 it can see the drive and they exchange packets also. i have attached photos of the MODULE INFORMATION CU320
Attachmentstep 7 Module Information.zip (173 Downloads) |
4/30/2021 5:38 AM | |
Joined: 5/12/2006 Last visit: 10/8/2024 Posts: 22399 Rating: (3017)
|
no telegrams defined in the cu, so no communication! |
4/30/2021 8:42 AM | |
Joined: 5/12/2006 Last visit: 10/8/2024 Posts: 22399 Rating: (3017)
|
you must add the exact same telegram configuration in starter and hw config |
4/30/2021 10:37 AM | |
Joined: 2/25/2016 Last visit: 9/13/2024 Posts: 9 Rating: (0) |
i have added the same telegram Config still not communicating AttachmentTelegram.zip (156 Downloads) |
Last edited by: Peterssss at: 04/30/2021 10:38:32 |
|
4/30/2021 10:54 AM | |
Joined: 5/12/2006 Last visit: 10/8/2024 Posts: 22399 Rating: (3017)
|
but different order of the telegrams in starter and hwconfig |