Hello, As jklm mentioned that card is not 'compatible' for Siemens PLC. But if you take ModbusTCP or Profibus that would be another story. Best regards, Hristo Mihalev |
3/17/2013 7:49 PM | |
Joined: 9/27/2006 Last visit: 3/22/2025 Posts: 12344 Rating:
|
Hello Mojy; To complete Umencho's remarks, the Altivar drives support a wide variety of communication protocols, some of which are easy to use for data exchanges with a S7 PLC. Ethernet/IP is not one of these (it is native to Controllogix PLCs from Rockwell). One example of compatible protocolsis Profibus-DP: ATV61/71 Profibus DP manual - VW3A3307 ATV61/71 Modbus TCP/IP manual - Daisy Chain Ethernet card - VW3A3310D S7 OpenModbus/TCP - IT4Industry - Siemens Hope this helps, Daniel Chartier |
Last edited by: dchartier at: 3/17/2013 7:58 PM |
|
3/22/2013 7:31 PM | |
Posts: 3 Rating:
|
Hi The altivar 61 and 71 is not too different. The communication of both them is same. This is a good toturial about this topic : Wizard for creating connection data for Modbus TCP communication. (Modbus TCP Wizard ) Thank you so much everyone, i hope this method work as well. GoodLuck |