2/6/2014 8:05 AM | |
Posts: 1368 Rating:
|
hello Niccou, there are some possibilties for a communication between S7-300 and S7-1500. It depends on, if you want to have a configured connection like S7 commucation or the way over the open commmunication. In this document http://support.automation.siemens.com/WW/view/de/78028908 you find the possibilites listed. If you want to have a s7 communiation, you must configure a unspecified connection in each projekt with the ip address of the partner.Have a look here in chapter 2.2.2 http://support.automation.siemens.com/WW/view/de/17628518 With the open communiucation (T blocks), you can use them in our program without any network configuration. Have fun... |