Hello, 1) It is possible to configure an S7 connection from a CPU3xx-PN towards a sytem equipped with a CP Lean. The CPU 3xx-PN takes initiative here, using PUT and GET The usage is explanined here: http://support.automation.siemens.com/WW/view/en/18610307 No extra program in the system with the Lean CP 2) a secondway is to declare the system with the Lean CP as IO device of the CPU3xx-PN acting as IO controller. The both sytems will echange data over fictive I/O In thewith the Lean CP, ou must use special PN - FCs See http://support.automation.siemens.com/WW/view/en/31764614 It seems that you have two separated projects. It is easier to put all together in one project. |
Best regards |
|
10/15/2009 3:20 AM | |
Posts: 2 Rating: (0) |
thank for yours answer.......i ll try configure the communication later today......tomorrow i ll have some news.....thak again |