Hello SAMIRKM further to the advise that was given, have a look at chapter 14.5.1 of the SIMATIC Fault-tolerant systems S7-400H manual and note the entry about GET/PUT at the end which states that: (Use) SFB 15 "PUT" and SFB 14 "GET" in the fault-tolerant system: Use two SFB 15 "PUT" blocks over two standard connections. successful. If possible, use the mechanisms of S7 communication for communication. |