11/10/2017 3:35 PM | |
Joined: 9/27/2006 Last visit: 9/22/2024 Posts: 12282 Rating: (2685) |
Hello jbeta; We have worked with Beckhoff Profibus couplers in some projects, mainsly with this one: https://www.beckhoff.com/english.asp?bus_terminal/bk3110.htm The coupler allows the Beckhoff I/O modules to act as a remote I/O slave for the Profibus master, and since the S7-300 CPUs mostly come with an integrated Profibus master interface it becomes very easy to bring them into the hardware configuration and the program of the PLC. In the same page you will find links to other models of Profibus couplers from Beckhoff, if you want to see other selections. If your PLC has an extension -2PN/DP in its descriptor, then you can also decide to use Profinet, with the Beckhoff I/O as part of a Profinet I/O station. Here is a product descrition page for a Beckhoff Profinet coupler module, with other similar product links at the bottom of the page. Hope this helps, Daniel Chartier |
This contribution was helpful to2 thankful Users |
11/10/2017 5:41 PM | |
Joined: 9/27/2006 Last visit: 9/22/2024 Posts: 12282 Rating: (2685) |
Hello The EK3100 is a Beckhoff PLC with Profibus interface; in this case it would be equivalent to a CPU 315-2DP. https://infosys.beckhoff.com/content/1033/ek3100/3974742923.html The BK3100 is a Profibus head module for a remote I/O station; it would be similar to a Siemens IM 153-2. That is why it would be esier tœ use a BK3100 to connect Beckhoff I/O modules to Siemens CPU over Profibus. Hope this helps, Daniel Chartier |
This contribution was helpful to1 thankful Users |
11/10/2017 6:22 PM | |
Joined: 9/28/2017 Last visit: 9/3/2024 Posts: 4 Rating: (0) |
Ah I see now. Your help has been invaluable. Thanks again! |