Hello Emin; Basically, you need to install the CP 343-1 in your rack properly, configure it in your PLC hardware (Step 7 HWConfig and Netproare the correct editors) and create communication blocks AG_SEND and AG_RECV (for example)to exchange data with a partner; data transferto/from the CPU over the backplane connections will be taken care of by the CPU's operating system. Here is some litterature that could be of help: CP 343-1 Lean installation/hardware manual: http://support.automation.siemens.com/WW/view/en/23643456 Siemens CPs Communication blocks Programming manual: http://support.automation.siemens.com/WW/view/en/30564821 Look at blocks AG_SEND and AG_RECV for Industrial Ethernet Hope this helps,Daniel Chartier |