7/15/2018 11:09 PM | |
Joined: 4/28/2015 Last visit: 3/21/2025 Posts: 16 Rating:
|
Hello dear experts, Please, how can i make communication between s7 1200 and Samkoon HMI SH-070HS, "ethernet", note that i already activated the get/put option in TIA portal, and select the s7 1200 driver in sktool, is it strange that in sktool it is required a port number for the s7 1200 ?? I'm using sktool 6.0...., best regardes ------------------------------------------------------------------------------------------ |
Last edited by: Abdi.Tlemcen at: 7/15/2018 11:12:54 PMLast edited by: Abdi.Tlemcen at: 7/15/2018 11:14:13 PMLast edited by: Jen_Moderator at: 7/16/2018 7:49:05 AMNew subject after splitting |
|
11/5/2018 9:06 PM | |
Joined: 4/28/2015 Last visit: 3/21/2025 Posts: 16 Rating:
|
Hello, Solved, just choose the port 102 for s7 1200. good day, |
This contribution was helpful to
1 thankful Users |