5/22/2019 9:03 AM | |
Posts: 3093 Rating:
|
How do you establish a MODBUS-RTU communication with STEP 7 (TIA Portal) for the SIMATIC S7-1200? |
5/22/2019 9:18 AM | |
Posts: 114 Rating:
|
Thank You But I am Not able to read data from my Schneider Em 6433, I Have Attached My ProgrammeAttachmentENERGY_MTR_MODBUS_RTU.zip (966 Downloads) |
5/22/2019 9:49 AM | |
Posts: 1283 Rating:
|
First did you verify you are able to read the Energy meter using PC software for Modbus? |
5/22/2019 10:10 AM | |
Posts: 114 Rating:
|
Dear Jay, Which pc software, do you have any sample backup. |
Last edited by: vicky bhau at: 05/22/2019 10:16:47 |
|
5/22/2019 10:17 AM | |
Posts: 1283 Rating:
|
There are many PC software available. You can try Modbus Master as in the attcahment. Modscan software and many trial software which can be used with PC software and USB to serial port cables for connection with PC to the energymeter. if you are directly trying to read the energy meter, you cant be sure whether the energy meter is already sending data or not. so always ensure with a PC software and then connect to PLC after you are sure your energy meter config is right.
AttachmentModbusMaster.zip (390 Downloads) |
5/22/2019 10:32 AM | |
Posts: 114 Rating:
|
THANK YOU JAY. |
5/22/2019 10:54 AM | |
Posts: 114 Rating:
|
I have attached image of status of mb_load & RX & TX on plc is continuously on . |
5/22/2019 11:10 AM | |
Posts: 3093 Rating:
|
Hello Vicky, How do you evaluate the status of system blocks in STEP 7 (TIA Portal)? When RX and TX are constantly on, there is a general error in parameterization / cable. Regards, |