4/2/2015 9:26 AM | |
Joined: 5/12/2006 Last visit: 4/28/2025 Posts: 22604 Rating:
|
Hello,
you must configure the D410 as I-Device on the S7-300 PLC. A application example you can finde here.
Regards |
4/2/2015 10:51 AM | |
Joined: 4/10/2009 Last visit: 10/23/2023 Posts: 94 Rating:
|
Dear Sir After pressing the link, I am not able to get the application example. Kindly help Thanks & Regards Prian |
4/2/2015 11:23 AM | |
Joined: 5/12/2006 Last visit: 4/28/2025 Posts: 22604 Rating:
|
try it again, it works here for me correctly or search for ID 38494882 in the Product Support.
Regards |