Hi TK1620, As far as I know, WinCC RT Advanced includes a Mitsubishi driver that allows you to communicate with Q-type and FX3U PLCs. Seems that FX5 can't be selected when creating the communication link but maybe you can try selecting FX3U option and see if communication works. Here you can find more information about how to configure this communication https://support.industry.siemens.com/cs/ww/en/view/109794203/136449058699 If I am not wrong, Mitsubishi PLCs integrates an OPC UA Server so if first methon does not work, maybe you can try with OPA UA communication configuring the WinCC RT Advanced as an OPC UA Client and the PLC as a server. https://support.industry.siemens.com/cs/ww/en/view/109794203/136031338123 |