9/11/2014 2:24 PM | |
Posts: 93 Rating:
Yes i have configured it from Starter. My issue is in HW CONFIG. How to establish it via PRofibus DP. Any tutorial for this??? |
9/11/2014 2:42 PM | |
Joined: 5/12/2006 Last visit: 2/2/2023 Posts: 21218 Rating:
Hello, install the GSD in HWConfig insert the GSD object in the HWConfig of the PLC project configure the telegramms which you have created in STARTER download the new HW Config to the PLC second question: already answered here regards Christoph |
9/11/2014 3:01 PM | |
Hello, here you can download the GSD(CU320 V2.6) After installing the GSD File in HWconfig you will find the GSD object in the HW Catalog PROFIBUS DP ->Additional Field Devices -> Drives -> SINAMICS Put the object SINAMICS S DXB to the PROFIBUS Subnet of the PLC in your project configure the telegrams like the config in starter done Regards Christoph |