11/6/2007 2:57 PM | |
Posts: 3 Rating:
|
Hello, I have trouble configurating a system that has to communicate with a Emerson Delta V by Profibus DP. The costumer asked me to provide 2 DP slaves in order to communicate, but I can not find a suitable slave for my system configuration. I'm using a redundant S7 414, a part of ET200M I/O and a part with ET200S I/O trough an Y-link (see attached configuration) and want to place the DP-slaves in a ET 200M rack. At this moment I also have a thread running for an error popup I get when trying to fit in a CP module in one of the ET200M racks [URL=/tf/WW/en/Posts/13177]"ZS capability error"[/URL] Is there anybody who is familiar with communication to a Delta V, or otherwise a simular communication? Any help is welcome. Regards, Werner Attachmenthardware.zip (679 Downloads) |
11/7/2007 4:54 PM | |
Posts: 5822 Rating:
|
Hello, I try to understand. You have a redundant H System on S7 side that needs to connected as a DP Master System to another DP MasterSystem that is also redundant (Delta V) and this has to be done on DP, am I right so far? If so I see a little mess, but a possible solution too. There is on SIMATIC side the possibility to use a so called Y-Link, this is a redundant DP Slave and connects to DP Masters Systems to single sided DP Slaves. On this side you can connect a DP/DP Coupler which is a Device that is DP Slave on both sides. There you can transfer up to 244 Bytes, if I remember right, in between the two Master Systems. I just wonder... is it not possible to do any other connection.... with TCP/IP for example? Best regards J_Bell |