Dear All, I am facing few problem during accessing the S120 series SINAMICS drive to our control room PC via Step-7.The project was created in older version of STARTER and so i have converted the project in our newer version of STARTER software. After setting PG/PC interface for PC ADAPTER MPI (AUTO) or TCP/IP(AUTO) a message window giving error info regarding communication failure. Though the Micromaster drive of this project is getting communication to our control room PC via Step-7 PLC on TCP/IP(Auto) protocol. kindly provide me the exact reason of this problem...is it due to firmware version of SINAMICS CU320 drive or something else..?? I am attaching the image of error message. thanks in advance..
AttachmentIMAGE.zip (113 Downloads) |
10/27/2013 12:42 PM | |
Posts: 14 Rating: (0) |
Dear Sir, I tried to open the project in old original format but the message window appear which shows no any option for openng the project in old version. Without pressing the Ok button ,project is not getting open.After Opening the project the SINAMICS Drive unit is not found ... I am Inserting the image of message /Error window. what to do sir..?? How can i update the FW of CF card .. Attachmentimage-2.zip (57 Downloads) |
10/28/2013 6:41 AM | |
Joined: 5/12/2006 Last visit: 10/2/2024 Posts: 22388 Rating: (3015)
|
Hello, the problem is not to open the project in new or old format. The problem is that th CU320 in the Projeect is Version V2.6 an the FW on he Target CF is V2.5. So anybody have give you a wrong project or have update the CU in the project but not the target! The FW V2.6 you can download here. Regards Christoph |