Hello every body, My problem is that in the connection betwen a Cpu 300 and Md720, this is disconnectd frecuently, in the manual MN_Sianut_Micro SC, in the page 57 says: Data loss between SINAUT MICRO SC and PLC Please make sure that you wait at least 5 to 10 seconds between two requests from SINAUT MICRO SC to the PLC. But, i dont know as do this, any person know? Thanks you for help me AttachmentMN_SINAUT-MicroSC_76.pdf (135 Downloads) |
11/4/2009 5:04 PM | |
Joined: 9/29/2005 Last visit: 12/16/2024 Posts: 313 Rating:
|
Hi, first of all: notice that your available documentation is dedicated to the S7-200 based solution. So you can transfer this content only to the Central Station side.
In SINAUT Micro SC (Start/SIMATIC/SINAUT Micro SC/Configuration) you can have several status-mechanism activated (Click on your configured station and press the "edit"-button). One of the status-monitoring option is "... with value update". This is to select and here you can enter the interval. Simple choose something above 15s (i would suggest >60s). Ok, now you will get all the values updated which are implemented in your OPC-client (Maybe WinCC flex or whatever). This means there must be no sending-intelligence at S7-300 side. All the values are fetched from the SINAUT Micro SC -side in combination with the FW of the MD720-3. Maybe this topic can help you furthermore: link cya |