HelloRDH, Have you changed the DIP switched on the second ET200M according to its DP address in the HW config.? Could you connect your PG/ES/Notebook to the Profibus network and detect the accessible nodes? Can you take the IM153 out of the rack (i.e. split the IM153 aside of IO modules)and test the network? Best regards, H-H
|
This contribution was helpful to
4 thankful Users |
5/17/2014 7:27 PM | |
Joined: 10/10/2010 Last visit: 5/26/2023 Posts: 299 Rating:
|
try to rplace the module it's defective |
This contribution was helpful to
1 thankful Users |
5/18/2014 3:32 AM | |
Posts: 3 Rating:
|
Hi H-H, I set the DIP switches to the same as the ones that they replaced. I have connected theLaptop top the network with the MPI adaptor and I can only see 2 nodes, the master and one one on the slave nodes, when I try to get the module information it says that it can not detect it (see attachment). I have also tried just the network with all the IO modules and still the same issue, I also took the one that I got working and put it in the place os the one that was not (I changed the DIP switches accordingly), and still it get the same outcome. Best Regards, RDH AttachmentZ:\Rig ET files\ET\Monitoring System\Monitoring System Fault 16-5-2014\Radio Room.jpg (53 Downloads) |